WELCOME TO RIVER DAVES PLACE

Price of upgrading a 100amp residential panel to 200amp. It’s gone up..

MeCasa16

Well-Known Member
Joined
May 29, 2018
Messages
1,674
Reaction score
3,405
I got 3 bids. All about the exact same. This is Seattle, but these prices seem absurd. $7200. Then add the fees for the electric company, another fee I couldn’t read what it was, nor was it explained. Then of course add tax. Total was $8997. They added an exterior box with shut off for the fire department and just a basic square D box on the inside. It’s a single story 1500 sq ft. House built in the 50’s. The house has some other wiring issues I inquired about. Mainly that it has junction boxes everywhere in the attic and everything seems to be connected. He said he could only rewire the house, doesn’t work in attics, and would need us to drop the whole ceiling. 20k estimate. 🤣🤣

F that. We need it done yesterday, so we will end up going up there and doing it ourselves.
 

SnoC653

Well-Known Member
Joined
Apr 30, 2008
Messages
242
Reaction score
416
This thread should be titled they are ripping us off because we are getting older. I put a 200 Amp box in my shop myself. I spent maybe $500 total on the project while the lowest estimate I got was $4,000. I may not have put in as many outlets as they were talking, but I can always add those. I did pay a retired electrician to tell me what to do so I wouldn't kill myself or burn down the shop.
 

FROGMAN524

Well-Known Member
Joined
Mar 16, 2013
Messages
5,812
Reaction score
10,712
Is 100amp normal? I thought 200 was the base, and people upgrade to 400, like we did.
Not in the 50s. My MIL had a ranch house built in early 50s with a 50A panel. It went out last week along with her heat pump and all together it was like $15,000 to fix.
 

MeCasa16

Well-Known Member
Joined
May 29, 2018
Messages
1,674
Reaction score
3,405
Is 100amp normal? I thought 200 was the base, and people upgrade to 400, like we did.
You probably have a much bigger house. This is only 1500 sq/ft. When it was built it didn’t have A/C or an electric furnace. As those things have been added it has outgrown its capacity.
 

MeCasa16

Well-Known Member
Joined
May 29, 2018
Messages
1,674
Reaction score
3,405
This thread should be titled they are ripping us off because we are getting older. I put a 200 Amp box in my shop myself. I spent maybe $500 total on the project while the lowest estimate I got was $4,000. I may not have put in as many outlets as they were talking, but I can always add those. I did pay a retired electrician to tell me what to do so I wouldn't kill myself or burn down the shop.
Im only 43. 🤣 But they are still ripping me off.
 

Ace in the Hole

Well-Known Member
Joined
Aug 15, 2020
Messages
6,342
Reaction score
15,016
That’s the cost of materials today.

I’m at 3500-4500. Depending on scenario
This is what we charged to do them on solar installs in Texas that needed to go to a 200A.

Not in the 50s. My MIL had a ranch house built in early 50s with a 50A panel. It went out last week along with her heat pump and all together it was like $15,000 to fix.
Back in Hawaii a lot of the old single wall homes built in the post war years were button meter and 50A. It was an undertaking to upgrade those houses 😅😅
 

hallett21

Well-Known Member
Joined
Nov 9, 2010
Messages
18,390
Reaction score
23,717
This is what we charged to do them on solar installs in Texas that needed to go to a 200A.


Back in Hawaii a lot of the old single wall homes built in the post war years were button meter and 50A. It was an undertaking to upgrade those houses 😅😅

I had one just nailed to some plywood “siding”. Removed the plywood and nailed it to a tree until Edison would come disconnect it lol
 

D19

Well-Known Member
Joined
Aug 13, 2018
Messages
2,469
Reaction score
4,920
Materials have shot way up! I've been out of construction for awhile and couldn't believe how much stuff went up at Walters.

I'm swapping it out myself and relocating. Just want someone to come move my meter and overhead feed to new panel. I don't feel like going up there to do it. Anyone want some side work? LOL
 

Backlash

Well-Known Member
Joined
Jan 14, 2011
Messages
14,580
Reaction score
28,459
Materials have shot way up! I've been out of construction for awhile and couldn't believe how much stuff went up at Walters.

I'm swapping it out myself and relocating. Just want someone to come move my meter and overhead feed to new panel. I don't feel like going up there to do it. Anyone want some side work? LOL
I thought SoCal Edison would come out and move your meter for you, no??
 

Joe mama

Well-Known Member
Joined
Oct 22, 2010
Messages
3,894
Reaction score
3,804
buddy of mine gave a quote the other day 4K with permit. He said he got beat by a guy on offer up 2200 no permit. This was in Rancho.
100A to 200A
 

TimeBandit

Well-Known Member
Joined
Sep 18, 2019
Messages
2,430
Reaction score
5,524
buddy of mine gave a quote the other day 4K with permit. He said he got beat by a guy on offer up 2200 no permit. This was in Rancho.
100A to 200A
Don't you need heavier wires run by the power company from the pole to the new 200A panel?

Or are we talking about a panel upgrade only, not a service upgrade??
 

Joe mama

Well-Known Member
Joined
Oct 22, 2010
Messages
3,894
Reaction score
3,804
Probably no arc fault breakers at that price. Used to pay 2k for a 200 amp upgrade until those came into play.
Haven’t had to upgrade existing branch circuits to arc fault on just a service upgrade. That could be a nightmare if Joe home owner or joe handyman was doing his own electrical installs.
 
  • Like
Reactions: TPC

Mandelon

Coffee makes me poop.
Joined
Sep 24, 2007
Messages
14,632
Reaction score
20,323
I used to get this done for $2500 only a few years ago. The ARC fault breakers are expensive, but that seems like giraffe pussy high.
 

NicPaus

Well-Known Member
Joined
Sep 15, 2010
Messages
14,210
Reaction score
15,146
Haven’t had to upgrade existing branch circuits to arc fault on just a service upgrade. That could be a nightmare if Joe home owner or joe handyman was doing his own electrical installs.
Guess it depends on the inspector. Have done few kitchen remodels that required panel upgrade for those stupid arc faults to work. Few inspectors that want everything arc fault. I hate those breakers.
 

TPC

Wrenching Dad
Joined
Sep 20, 2007
Messages
31,630
Reaction score
25,278
Tesla wanted $7.700 for the panel placement and hook up alone. Nothing else.

Lucky the wire to the street was adequate but I hear if not it’s on Edison to pull correct gauge.

Found a Cracker Jack electrician did it for
half that plus did a days worth of other elect work the wife wanted done. All kinds of crazy electrical shit Ali had him jumping through a fiery hoop.

The hard part was finding a stucco patch guy to sweeten up the install. The guy I finally got was fantastic. Couldn’t tell a thing.

Read that: finally. Hard as hell to get someone so it wouldn’t look like a soup sandwich.
 
Last edited:

LuauLounge

Well-Known Member
Joined
Jul 24, 2010
Messages
3,588
Reaction score
6,763
I'm not one to frivolously toss dollars around, but I wouldn't hire an unlicensed electrician with no permit from OfferUp to do a panel upgrade.
 

hallett21

Well-Known Member
Joined
Nov 9, 2010
Messages
18,390
Reaction score
23,717
Haven’t had to upgrade existing branch circuits to arc fault on just a service upgrade. That could be a nightmare if Joe home owner or joe handyman was doing his own electrical installs.

I’ve had it on almost all of them for 2-3 years now. Very frustrating
 

Joe mama

Well-Known Member
Joined
Oct 22, 2010
Messages
3,894
Reaction score
3,804
Guess it depends on the inspector. Have done few kitchen remodels that required panel upgrade for those stupid arc faults to work. Few inspectors that want everything arc fault. I hate those breakers.
I can see them required if there was a Kitchen remodel along with service change or new kitchen circuits.
 
Last edited:

sintax

Well-Known Member
Joined
Mar 7, 2008
Messages
7,052
Reaction score
11,769
That’s the cost of materials today.

I’m at 3500-4500. Depending on scenario

I have someone doing mine in Riverside for $3500, starting in a couple of weeks. Just got the disconnect date from Edison
 

farmo83

Well-Known Member
Joined
Jun 9, 2008
Messages
2,512
Reaction score
2,763
Isn't this all for nothing unless you have a big enough wire running to the house from the grid ?

I wouldn't think a 200 amp panel hooked up to a wire that can only care 50 amps from the power company would do much ?

Or are they all generally oversized and you just pick what service you want/need?
 

JL95

Well-Known Member
Joined
Dec 21, 2021
Messages
816
Reaction score
1,799
I got mine done for around $2400-$2800 permitted I don't exactly remember. The hardest part was i got tagged for a Meter spot from edison for no reason so coordinating with the city and Edison was a nightmare. Took about a month to line them all up. Sparky got it done in a few hours when it was show time.

Also be very cautious of offerup work my stucco guy was so bad lmao. Easiest money he's ever made.
 

hallett21

Well-Known Member
Joined
Nov 9, 2010
Messages
18,390
Reaction score
23,717
Isn't this all for nothing unless you have a big enough wire running to the house from the grid ?

I wouldn't think a 200 amp panel hooked up to a wire that can only care 50 amps from the power company would do much ?

Or are they all generally oversized and you just pick what service you want/need?

When you pull the permit the building department notifies the utility. It’s the utilities responsibility to upgrade their side of service. This is assuming you’re in a normal neighborhood and not 10 miles from a street.

You also need to give the building department a load calculation if you are adding more load to the service. If you’re changing a 100amp for a 200amp panel with no additional circuits the utility won’t upgrade their line.

An example of the permit application.

F9A95E0C-BC90-4316-AEAF-9172E4CE0DFB.png
AD674F43-CED4-4D46-9B65-905009B92575.png
 

NicPaus

Well-Known Member
Joined
Sep 15, 2010
Messages
14,210
Reaction score
15,146
I got mine done for around $2400-$2800 permitted I don't exactly remember. The hardest part was i got tagged for a Meter spot from edison for no reason so coordinating with the city and Edison was a nightmare. Took about a month to line them all up. Sparky got it done in a few hours when it was show time.

Also be very cautious of offerup work my stucco guy was so bad lmao. Easiest money he's ever made.
They do a meter spot for Edison or LADWP. Need the meter location to move forward with permit. Usually the same location but not always. If not the same then it can get pricey as you would need a sub panel unless you are doing a full rewire.
 

D19

Well-Known Member
Joined
Aug 13, 2018
Messages
2,469
Reaction score
4,920
They do a meter spot for Edison or LADWP. Need the meter location to move forward with permit. Usually the same location but not always. If not the same then it can get pricey as you would need a sub panel unless you are doing a full rewire.

Back when I did a lot of TI, we would use pull boxes / gutters to relocate panels/etc.

I don't the rules these days but can't you just pull the home runs into the attic and run a box to the new location?
 

JL95

Well-Known Member
Joined
Dec 21, 2021
Messages
816
Reaction score
1,799
They do a meter spot for Edison or LADWP. Need the meter location to move forward with permit. Usually the same location but not always. If not the same then it can get pricey as you would need a sub panel unless you are doing a full rewire.
I am not too familiar with any of this, the only thing I'm running on was my electrician telling me out of the few hundred panel change outs he has done they have only done a handful of meter spots, mainly only when changing location to verify it is acceptable. IDK he was very surprised about it. The location stayed the same for me.
My panel caught fire from my AC condenser breaker arcing when it didn't fully reset. Shit show. 1990 panel had its time
 

MPHSystems

Hallett 240
Joined
Sep 10, 2021
Messages
4,004
Reaction score
9,912
I got 3 bids. All about the exact same. This is Seattle, but these prices seem absurd. $7200. Then add the fees for the electric company, another fee I couldn’t read what it was, nor was it explained. Then of course add tax. Total was $8997. They added an exterior box with shut off for the fire department and just a basic square D box on the inside. It’s a single story 1500 sq ft. House built in the 50’s. The house has some other wiring issues I inquired about. Mainly that it has junction boxes everywhere in the attic and everything seems to be connected. He said he could only rewire the house, doesn’t work in attics, and would need us to drop the whole ceiling. 20k estimate. 🤣🤣

F that. We need it done yesterday, so we will end up going up there and doing it ourselves.
I wish I was an electrical contractor, I could do the job for 1/2 that price…


Oh wait, I am and I can!

But not in Seattle.
 

hallett21

Well-Known Member
Joined
Nov 9, 2010
Messages
18,390
Reaction score
23,717
Back when I did a lot of TI, we would use pull boxes / gutters to relocate panels/etc.

I don't the rules these days but can't you just pull the home runs into the attic and run a box to the new location?

If you can find them yes lol. They always seem to be running through the worst spots though. Another option is using a “dog house” with a junction box at the old panel location.
 
  • Like
Reactions: D19

hallett21

Well-Known Member
Joined
Nov 9, 2010
Messages
18,390
Reaction score
23,717
I am not too familiar with any of this, the only thing I'm running on was my electrician telling me out of the few hundred panel change outs he has done they have only done a handful of meter spots, mainly only when changing location to verify it is acceptable. IDK he was very surprised about it. The location stayed the same for me.
My panel caught fire from my AC condenser breaker arcing when it didn't fully reset. Shit show. 1990 panel had its time

A lot of the old panel locations now violate current code or due to development are in bad service entrance locations. So the utility now spots the location to make sure their service entrance cable isn’t in a bad spot.

A couple ones I’ve dealt with included

Wires going over someone else’s property to get to your service.

Wires too low over driveways

Wires crossing the entire home in the air to get to the service mast.

Wires crossing a pool 🍻

Edit. My inspectors won’t even walk onto the property if I don’t show them the meter spot.
 
Last edited:

blownmirage

Well-Known Member
Joined
Mar 18, 2013
Messages
48
Reaction score
41
Had a friend that hired some backyard electrician to do his panel upgrade, didn't work out so well, fried fridge, furnace and something else when they turned it on,
can't remember everything, backyard electrician just walked away and he had to hire a electrical contractor and fix all that was wrong, buy a new fridge, and circuit board for furnace, ended up costing him about 2 1/2 times more. He won't ever do that again
 

badgas

Well-Known Member
Joined
Jul 30, 2020
Messages
1,745
Reaction score
3,491
I was quoted $3,500 for a 200 amp panel upgrade This includes patching stucco paint etc.

We charge $2,550 with a Solar install.
 

dspracing

Well-Known Member
Joined
Apr 6, 2010
Messages
1,644
Reaction score
3,030
buddy of mine gave a quote the other day 4K with permit. He said he got beat by a guy on offer up 2200 no permit. This was in Rancho.
100A to 200A
Is he going to try doing this with no permit? My buddy told me we could do the same thing, he’s a union electrician.

I call Edison for the meter unlock which they perform right away no questions asked. We get the job done and ask them to come back and reterminate the lines at the mast and lock the meter…. Oh you did a panel upgrade??? Well you’ve got X days to get this permitted and signed off before we shut your power off.

I don’t remember the exact time but I think it was like 7 days. That was a big oh shit moment.

Raced down to the city, pulled permit, got it signed off and sent the proof to Edison. They came out a few days later pulled a new line from the pole and locked the meter.
 

Joe mama

Well-Known Member
Joined
Oct 22, 2010
Messages
3,894
Reaction score
3,804
Is he going to try doing this with no permit? My buddy told me we could do the same thing, he’s a union electrician.

I call Edison for the meter unlock which they perform right away no questions asked. We get the job done and ask them to come back and reterminate the lines at the mast and lock the meter…. Oh you did a panel upgrade??? Well you’ve got X days to get this permitted and signed off before we shut your power off.

I don’t remember the exact time but I think it was like 7 days. That was a big oh shit moment.

Raced down to the city, pulled permit, got it signed off and sent the proof to Edison. They came out a few days later pulled a new line from the pole and locked the meter.
I’ve done plenty without permits back in the day without permits. They didn’t have meter locks.
 

Taboma

Well-Known Member
Joined
Apr 4, 2008
Messages
15,577
Reaction score
22,477
I’ve done plenty without permits back in the day without permits. They didn’t have meter locks.
Back in 'That Day', I may have had a couple of these in my bag of tricks. 😁 'That Day', was a ways back, like 53 years or so, before they got all sophisticated and shit. 😂


I was checking with my kid the other day on a panel upgrade from 100A to 200A for a solar install, about $ 3,500. BUT, that's only to increase the buss rating to at least 125A, if the solar was large enough to require a 50A breaker.
The home I was inquiring about, had an UG service, which in order to increase the conduit size to accommodate increasing service capacity to 200A, would easily more than double that cost

DUMB SHIT EDIT ---- Failure to attach image oops. 🤗 When life was simple. 😁
MS.JPG
 
Last edited:

Sleek-Jet

Well-Known Member
Joined
Sep 20, 2007
Messages
13,313
Reaction score
16,754
Man, you guys in Cali are so screwed. Out here Electricians routinely pull meters and then call us to reseal the base after the fact.

Building department rarely gives a heads up on permits for panel upgrades. Wild how different it is in other parts of the country.
 
Top