Both stopped working today, it is a Trane system about 15 years old. Power to and through the relay switch, red and blacks wires are 118v seen in the pic.

Any ideas?

1598575746598.png

trane.jpg
 
Last edited:

Joe mama

Well-Known Member
Joined
Oct 22, 2010
Messages
3,863
Reaction score
3,731
Okay I will bite, 240v between BLK and red at bottom of relay?
 

Flying_Lavey

Dreaming of the lake
Joined
Feb 13, 2008
Messages
21,190
Reaction score
18,815
Well that relay is doing nothing anymore. It's for a hard start kit that looks like the cap went bad and was just pulled out instead of replaced.

Betcha you got a non-op fan motor so the compressor internal thermal overload tripped resulted in both not running. If not....

Check your run cap (big on is compressor and small is fan motor) between the C and HERM terminals for the compressor

Check your voltage between both legs of power

Check amp draw immediately after cycling power (see what the in-rush amps are)

Sent from my LM-G710VM using Tapatalk
 

90 Laveycraft

SBC/Jet..Oh hell ya!
Joined
Sep 22, 2009
Messages
611
Reaction score
330
Think FL is dead on...inop external fan motor/capacitor, compressor has a overload protector that opens when over heated..is compressor smoking hot?
 

Joe mama

Well-Known Member
Joined
Oct 22, 2010
Messages
3,863
Reaction score
3,731
If your getting 120 to ground on each leg and contractor is not pulled in that’s good. If contractor is pulled in one leg can feed through compressor to o5her leg.
 

Angler

Tritoon Racing
Joined
May 4, 2012
Messages
5,998
Reaction score
14,680
Think FL is dead on...inop external fan motor/capacitor, compressor has a overload protector that opens when over heated..is compressor smoking hot?
wasn't here when it stopped working
 

Flying_Lavey

Dreaming of the lake
Joined
Feb 13, 2008
Messages
21,190
Reaction score
18,815
wasn't here when it stopped working
It resets and runs after it cools down. If the contactor is pulled in like that and it's burning hot, thermal overload and is a condensing fan issue (doesn't look like, and I doubt there is a fan cycle control in there).

Sent from my LM-G710VM using Tapatalk
 

Shlbyntro

Ultra Conservative
Joined
May 27, 2018
Messages
7,744
Reaction score
22,577
My guess would be the $500 capacitor if I had a hunch....

 

Flying_Lavey

Dreaming of the lake
Joined
Feb 13, 2008
Messages
21,190
Reaction score
18,815
If your getting 120 to ground on each leg and contractor is not pulled in that’s good. If contractor is pulled in one leg can feed through compressor to o5her leg.
This is true. 120 on each leg is good but you need to make sure there is 240 to make sure there isn't any circuit issues. The compressor being super hot or not (like cannot keep your hand on top of it) would be the tell tale what the issue likely is.

Sent from my LM-G710VM using Tapatalk
 

90 Laveycraft

SBC/Jet..Oh hell ya!
Joined
Sep 22, 2009
Messages
611
Reaction score
330
My guess would be the $500 capacitor if I had a hunch....

Lol
 

Angler

Tritoon Racing
Joined
May 4, 2012
Messages
5,998
Reaction score
14,680
My guess would be the $500 capacitor if I had a hunch....

the fan capacitor?
 

Angler

Tritoon Racing
Joined
May 4, 2012
Messages
5,998
Reaction score
14,680
Will the fan or compressor, start without each other?
 

Shlbyntro

Ultra Conservative
Joined
May 27, 2018
Messages
7,744
Reaction score
22,577
the fan capacitor?

One in the same on my unit and yours. On mine, the fan leg of the capacitor went out and even though the compressor leg was still good, the compressor was going into overheat protection because the fan wasn't running.
 

Flying_Lavey

Dreaming of the lake
Joined
Feb 13, 2008
Messages
21,190
Reaction score
18,815
Will the fan or compressor, start without each other?
Not on 15 year old Trane...if all is working correct..
This.... And, the fan can continue to run without the compressor as long as the thermostat is calling for cooling (contactor pulled in indicates it is calling for cooling).

Sent from my LM-G710VM using Tapatalk
 

Angler

Tritoon Racing
Joined
May 4, 2012
Messages
5,998
Reaction score
14,680
One in the same on my unit and yours. On mine, the fan leg of the capacitor went out and even though the compressor leg was still good, the compressor was going into overheat protection because the fan wasn't running.
but will the compressor run without the fan if it is cooled down. Like I said, it's been for several hours.
 

Flying_Lavey

Dreaming of the lake
Joined
Feb 13, 2008
Messages
21,190
Reaction score
18,815
One in the same on my unit and yours. On mine, the fan leg of the capacitor went out and even though the compressor leg was still good, the compressor was going into overheat protection because the fan wasn't running.
Negative ghost rider. His fan run cap has already been changed. As well as the fan motor. It is the same run cap right next to the large combo cap.

Sent from my LM-G710VM using Tapatalk
 

Shlbyntro

Ultra Conservative
Joined
May 27, 2018
Messages
7,744
Reaction score
22,577
Negative ghost rider. His fan run cap has already been changed. As well as the fan motor. It is the same run cap right next to the large combo cap.

Sent from my LM-G710VM using Tapatalk

My bad, didn't see that little tike down there, please disregard :D
 
Last edited:

90 Laveycraft

SBC/Jet..Oh hell ya!
Joined
Sep 22, 2009
Messages
611
Reaction score
330
You need a completely cooled down unit as your 110 meter aint gona get it.
Be at the unit after cool down..have someone start it, or push in the contactor and observe...does the compressor only start?
Do both start?

Thinking just call the guy!
 

Angler

Tritoon Racing
Joined
May 4, 2012
Messages
5,998
Reaction score
14,680
If anyone is near San Dimas, come on by.. 😃
 

90 Laveycraft

SBC/Jet..Oh hell ya!
Joined
Sep 22, 2009
Messages
611
Reaction score
330
Want a new one...I have 500 at work...
 

Attachments

  • 20200827_075710.jpg
    20200827_075710.jpg
    188.4 KB · Views: 74

SoCalDave

Well-Known Member
Joined
Jul 1, 2011
Messages
13,279
Reaction score
30,806
My guess would be the $500 capacitor if I had a hunch....

Was just waiting for that post...
 

Angler

Tritoon Racing
Joined
May 4, 2012
Messages
5,998
Reaction score
14,680
You need a completely cooled down unit as your 110 meter aint gona get it.
Be at the unit after cool down..have someone start it, or push in the contactor and observe...does the compressor only start?
Do both start?

Thinking just call the guy!
The compressor won't run.
 
Last edited:

90 Laveycraft

SBC/Jet..Oh hell ya!
Joined
Sep 22, 2009
Messages
611
Reaction score
330
We can only sell to licensed ac contractors w/proper freon certs...
Price will vary dramatically, contractor to contractor.
Go with longevity in trade, reviews, get several bids for replacement.
 

Flying_Lavey

Dreaming of the lake
Joined
Feb 13, 2008
Messages
21,190
Reaction score
18,815
The compressor won't run.

AL 909 322-9923
Do you have a laser temp gun? If so, gun the top of the compressor and see what temperature it is. 90 Lavey is right, it can take several hours to cool down with no fan running.

Sent from my LM-G710VM using Tapatalk
 

Angler

Tritoon Racing
Joined
May 4, 2012
Messages
5,998
Reaction score
14,680
That has worked before, but it hasn't run in hours, nothing is hot.
 

Flying_Lavey

Dreaming of the lake
Joined
Feb 13, 2008
Messages
21,190
Reaction score
18,815
That has worked before, but it hasn't run in hours, nothing is hot.
If nothing is hot then you really need a 240v capable meter to diagnose further.

I'd also check the voltage across the contacts on each leg to make sure the contactor contacts are still good.

Assuming the contacts are still good, the compressor is likely bad from either a burnout or an open winding, likely caused by a failed condenser fan motor.

Sent from my LM-G710VM using Tapatalk
 

90 Laveycraft

SBC/Jet..Oh hell ya!
Joined
Sep 22, 2009
Messages
611
Reaction score
330
I would replace a 15 year old York(prob 10 -12 Seer), if compressor is out. If simple fix...run it!
Call the guy. Reputable company only....
 

Angler

Tritoon Racing
Joined
May 4, 2012
Messages
5,998
Reaction score
14,680
I would replace a 15 year old York(prob 10 -12 Seer), if compressor is out. If simple fix...run it!
Call the guy. Reputable company only....
16 seer
Have a buddy that might help pm
I have someone coming out tomorrow. Thanks for all the help guys.