try calling done-right electrical here in havasu. 928) 453-5255 he does alot of automation type sparky work.
Had to beat it into their young minds, test phase to phase, not phase to ground to test for potential.
I was deinstalling a panel board fed by a 480 volt 2000 amp bolted pressure switch one sunny day, and the plant electrician assured me it was deenergized. The switch was open. I checked for voltage on the load side phase to phase, and there was no voltage. I was about to proceed, but decided to check phase to ground.
To my surprise, the B phase was hot, but A and C were not. The bolt that fastened the B phase knife switch to the dielectric crossbar had fallen out, so when the switch was opened that phase stayed hot. It was a real eye opener.
I’m thinking maybe if the movers were rough with the machine it’s possible something was jarred loose, out of calibration / alignment / adjustment, etc. This machine no doubt has micro switches / sensors and the like requiring close tolerance adjustment specs.I pulled this new to us piece of equipment out of a lab in Denver 3 years ago and it has been in storage since.
The clear "cube relays are typically only used on the control side as they do not have a very high load rating. Like others have said, I'd love to see a wiring diagram cause even though I really do not have the slightest clue about the different types of transformers and what not, I can sww by how you are describing the issue that it is most likely a control issue. Id first check at those contactors that are pulling in if they have proper power going in AND out of it.When we try to start the motor we can see a couple of contactors pulling in but nothing happening on the clear relays.
speaking of high legs; "hey look at all these spare spaces in the panel", said the apprentice. "every third one's a spare! we can land the new lighting circuits here and here." lol what do you think happened next? yes the company owner's son did this and spent quite a bit of time replacing new but "slightly used" fixture parts.
now that thread has hit two pages we require an answer as to what the solution was to this problem
Since I recall you doing utility work in the SDG&E area, where is it still currently common to find 240 Delta on the customer side ? I found it increasingly uncommon after the later 70's, except older industrial areas of LA or strictly on the customer side, again in older plants.
Thank you a good control guy can look at that panel and figure out the problem without a schematicOk, I have an automation/controls guy coming tomorrow. Will update when I know more...
Installed a lot of those back in the day! Ours had the the flux dingleberry back extractor without the high leg..Maybe this will help
Thank you a good control guy can look at that panel and figure out the problem without a schematic
Any news? Curious to hear how it turned out.Ok, I have an automation/controls guy coming tomorrow. Will update when I know more...
Without a schematic and a sequence of operation it’s like a dog chasing its tail, eventually he catches it just to chase it again.
I found an industrial automation guy in Portland that has worked on these exact machines for a competitor of ours in the past and even moderinized them in a couple of cases. He is going to fly down next Thursday and dive in.Any news? Curious to hear how it turned out.
... but what happened to the person that was to check it out today?I found an industrial automation guy in Portland that has worked on these exact machines for a competitor of ours in the past and even moderinized them in a couple of cases. He is going to fly down next Thursday and dive in.
Will keep you updated.
Curious who this is?I found an industrial automation guy in Portland that has worked on these exact machines for a competitor of ours in the past and even moderinized them in a couple of cases. He is going to fly down next Thursday and dive in.
Will keep you updated.
I found an industrial automation guy in Portland that has worked on these exact machines for a competitor of ours in the past and even moderinized them in a couple of cases. He is going to fly down next Thursday and dive in.
Will keep you updated.
I felt more comfortable using a guy that has worked on similar equipment. We'll see how it works out.... but what happened to the person that was to check it out today?
I was deinstalling a switchboard fed by a 480 volt 2000 amp bolted pressure switch one sunny day, and the plant electrician assured me it was deenergized. The switch was open. I checked for voltage on the load side phase to phase, and there was no voltage. I was about to proceed, but decided to check phase to ground.
To my surprise, the B phase was hot, but A and C were not. The bolt that fastened the B phase knife switch to the dielectric crossbar had fallen out, so when the switch was opened that phase stayed hot. It was a real eye opener.
I joined that club at airport towers working on a exit sign guy I was working on them turned them back on when he was done fixing his sign . never trust anyone to control the powerYears ago, working on a 100hp blower, and trusting another guy, is how I ended up a member of "The 480 Club".
Something you never forget......
High leg is nothing to mess with and its killed alot of electrician. Deep tunnel project uses it for there pumps cause when the motor shorts out it goes directly to ground with the high leg.
Years ago, working on a 100hp blower, and trusting another guy, is how I ended up a member of "The 480 Club".
Something you never forget......
Im in the 460 club. Working on a good size package unit trying to locate a control circuit short and pulled the bonehead move of forgetting the line voltage was still hot. Went leg A to B. Luckily I was working by my tried and true practice of being somewhat off balance so when the joice went through, my muscles tightened and I fell away from the panel.Years ago, working on a 100hp blower, and trusting another guy, is how I ended up a member of "The 480 Club".
Something you never forget......
Im in the 460 club. Working on a good size package unit trying to locate a control circuit short and pulled the bonehead move of forgetting the line voltage was still hot. Went leg A to B. Luckily I was working by my tried and true practice of being somewhat off balance so when the joice went through, my muscles tightened and I fell away from the panel.
Yeah, never worked on anything more than 460 volt myself. That's some crazy big shit! I've had my hands inside many chiller and refrigeration rack panels that were 460v and up to 1000 amp while live and never got bit there. Just when I was working on a small 7 ton package unit.A newer tech from Siemens Building Controls, was working on a chiller at the Qualcomm central plant. Opened the floor standing cabinet, grabbed his Fluke to check for voltage. The large yellow and black labels on the cabinets door showed ----- "Caution, 4 60 Volts ". Imagine his surprise (And luck) when the Fluke meter that he had hanging on the open door exploded when he touched the leads to the terminals. Shaken, but OK, he was obviously quite puzzled as to why his Fluke had violently smoked . Checking again, sure enough, labels showed "Caution 4 60 Volts." Found the plant foreman and inquired, imagine his 2nd surprise when he was informed "Oh yeah, the "1" fell off and we haven't gotten around to putting a new one on" Suddenly, it all made sense. [emoji2959]
He's damned lucky (As was Qualcomm) he or somebody else wasn't holding the meter. I saw the meter, they put it in a display box at the Siemens branch as a reminder to others, if something seems wrong, like in this case, the gap between the 4 and the 6, verify, verify, verify.
Wasn't 460 volt, but 4160 volt, details, details.
Its a color film processor. When it is running, it will process about 500 rolls per day through this one. It is replacing a lower capacity machine currently in use.what is this thing we are working on here anyway? inquiring minds want to know.
A newer tech from Siemens Building Controls, was working on a chiller at the Qualcomm central plant. Opened the floor standing cabinet, grabbed his Fluke to check for voltage. The large yellow and black labels on the cabinets door showed ----- "Caution, 4 60 Volts ". Imagine his surprise (And luck) when the Fluke meter that he had hanging on the open door exploded when he touched the leads to the terminals. Shaken, but OK, he was obviously quite puzzled as to why his Fluke had violently smoked . Checking again, sure enough, labels showed "Caution 4 60 Volts." Found the plant foreman and inquired, imagine his 2nd surprise when he was informed "Oh yeah, the "1" fell off and we haven't gotten around to putting a new one on" Suddenly, it all made sense.
He's damned lucky (As was Qualcomm) he or somebody else wasn't holding the meter. I saw the meter, they put it in a display box at the Siemens branch as a reminder to others, if something seems wrong, like in this case, the gap between the 4 and the 6, verify, verify, verify.
Wasn't 460 volt, but 4160 volt, details, details.
A newer tech from Siemens Building Controls, was working on a chiller at the Qualcomm central plant. Opened the floor standing cabinet, grabbed his Fluke to check for voltage. The large yellow and black labels on the cabinets door showed ----- "Caution, 4 60 Volts ". Imagine his surprise (And luck) when the Fluke meter that he had hanging on the open door exploded when he touched the leads to the terminals. Shaken, but OK, he was obviously quite puzzled as to why his Fluke had violently smoked . Checking again, sure enough, labels showed "Caution 4 60 Volts." Found the plant foreman and inquired, imagine his 2nd surprise when he was informed "Oh yeah, the "1" fell off and we haven't gotten around to putting a new one on" Suddenly, it all made sense.
He's damned lucky (As was Qualcomm) he or somebody else wasn't holding the meter. I saw the meter, they put it in a display box at the Siemens branch as a reminder to others, if something seems wrong, like in this case, the gap between the 4 and the 6, verify, verify, verify.
Wasn't 460 volt, but 4160 volt, details, details.
Success!!!
We determined when the install tech hooked up the wires (which are labeled, but hard to read due to age) he mixed one of the safety switches labeled U for one of the water solenoid switches labeled W. The reason that sometimes we would get power to that switch was when the program called for water from one of the solenoids at different intervals.
Like I said control guy could figure it outSuccess!!!
So I had a guy come down from Oregon that is familiar with these machine's electronics. In fact, he has updated a few to more modern controls.
Super nice guy named Paul. He is semi-retired and works often in the winery business with their industrial controls, including a lot of Italian equipment.
Even though we didn't have this machine's schematics, we had a set to our sister machine which is similar, but more complex. It took quite a few hours for him to find the issues with most of his time going over the schematics and staring at the controls. There were 2 issues preventing the machine from running. Once he verified the motor would run if he jumped it, it was then a matter of finding why it was not getting a signal to run. When we were originally troubleshooting the message on the display indicated that a safety was possibly tripped. The installation tech and I jumped the safety switches at the switches, but it still did not run so we dismissed that angle.
Paul eventually found different power readings at the 2 safety switches, but randomly. We determined when the install tech hooked up the wires (which are labeled, but hard to read due to age) he mixed one of the safety switches labeled U for one of the water solenoid switches labeled W. The reason that sometimes we would get power to that switch was when the program called for water from one of the solenoids at different intervals. So, he switched the wiring and fired it up. But it still would not start unless he jumped the safety switches at the panel. We then determined that one of the coiled cords for the safety switches was intermittent as well. I'll order some new cords and switches and we should be good.
It was interesting watching him work in a methodical fashion and just breaking down all the inputs and outputs to see how it works. Paul immediately dismissed the high leg concept that the tech wanted.
Here is a video of it running. Note that the guards are off and the operator safety devices are not installed yet. There are still air and nitrogen lines to hook up as well. These are operated in complete darkness by the operator. We do have some infrared scopes, but those cannot always be used if we are running any type of film stock that would be affected by that wavelength.
Dropbox
www.dropbox.com
The installer had to attach lots of wires. Pretty much everything. He just mixed the ones labeled U and W.If you had mentioned your installer had wired remote switches to the controls I would have jumped all over that as the reason the machine wouldn't run!
Yep!Like I said control guy could figure it out
We process Black & White, C-41 (color negative) and E-6 (color slide) films. We have 3 dip and dunk machines like or similar to this and 2 'leader card' style machines that you might have seen in Costco type operations. We run 1000+ rolls per day at our San Clemente facility and about 150 per day in a contract facility in Florida. Even though all film arrives analog, it leaves digitized and delivered via our website.So what type/ who are you processing film for? More info on the machine would be cool.
I took photo in high school and used my dad's old school Nikon SLR that was 100% manual. I still prefer it to the modern digital SLR's. But the convenience and operating costs make it kinda hard to justify (buying film all the time versus cheap digital storage and the amount of pictures one can take at once on a digital versus a film are big factors.We process Black & White, C-41 (color negative) and E-6 (color slide) films. We have 3 dip and dunk machines like or similar to this and 2 'leader card' style machines that you might have seen in Costco type operations. We run 1000+ rolls per day at our San Clemente facility and about 150 per day in a contract facility in Florida. Even though all film arrives analog, it leaves digitized and delivered via our website.
There is still a subset of photographers that prefer film, or just an analog look. Many wedding photographers prefer film as skin tones are still superior to most digital applications. Wedding photographers can also charge a premium over digital shooters. We don't do much wedding work as there are a handful of labs that specialize in that market as it requires a lot of handholding. Our market is primarily film enthusiasts and wholesale work for other retailers. Film sales have actually been increasing over the past several years and is similar to the vinyl record resurgence.
Here is a link to a sales brochure on a Refrema. The one we were having issues with is a smaller model, however, our black and white machine is similar to the one in the brochure, but with fewer tanks as it is a shorter process.
Dropbox
www.dropbox.com